Outdoors Belkin UPS acting up!!!

Hi, I have a Belkin UPS F6C525-ser.....I just noticed that if I unplug the power it gives me 110v from battery power for 1 second, then beeps twice and shuts off.

I unpluged everything and tried again and it worked, but as soon as I connected something, like the transformer of my external modem (which uses a tiny amount of power), it shut down.

I guess that as long as there is no drain in the current it works...

At first I though it was the battery, so I pulled it out and checked with a voltimeter and is holding steady at 12.8V, I hooked up a 12v fan to the leads of the battery and the voltaje remained steady at 12.7v all along.
So I don't think the problem is the battery.....it seems fully charged.....

Any ideas???

I know these are pretty hard to open.....I opened one a couple of months ago and almost broke it off..

Mr. NoOne is offline   Reply With Quote
Old 01-09-2004, 09:15 PM   #2 (permalink)
Registered User
 
Bovon's Avatar
 
Join Date: Oct 2001
Location: Georgia
Posts: 2,233
Bovon is on a distinguished road
Most of the decent UPS's come with programmable software. There would be a serial connector to the machine...and when the software is loaded, there will be some settable things. Not being familiar with the Belkin, I do not have a clue.

Sure sounds like battery failure to me tho.. the current drain when connected to the computer would be several amps...where as the 12 volt DC fan drew only an amp (maybe).

Could also be some kind of bad connection in the system somewhere..hard to tell.
Bovon is offline   Reply With Quote
Old 01-09-2004, 09:51 PM   #3 (permalink)
Registered User
 
mlee97's Avatar
 
Join Date: May 2002
Location: East Tennessee
Posts: 142
mlee97 is on a distinguished road
12.7 volts is too low for a charged battery, should read about 13.4 volts fully charged. Battery problem.
mlee97 is offline   Reply With Quote
Old 01-09-2004, 10:08 PM   #4 (permalink)
sam
Registered User
 
sam's Avatar
 
Join Date: Dec 2002
Location: SOUTH FLA
Posts: 786
sam is on a distinguished road
i have a belkin 1200va UPS and my batery voltage is 26.8 volts so i would assume that its time to change the battery. mine reccomends to change every 3 years
sam is offline   Reply With Quote
Old 01-09-2004, 10:15 PM   #5 (permalink)
Registered User
 
HfdWolfPack's Avatar
 
Join Date: Oct 2001
Location: CT (between NY&MA)
Posts: 886
HfdWolfPack is on a distinguished road
I had a Belkin 650va work for two power outages....then on the third and fourth(more like brown-outs), it just quit and made my subwoofer hummmmm.
It was still under warranty and Belkin is sending me an 800va to replace it:ccol:
HfdWolfPack is offline   Reply With Quote
Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Most Active Discussions

Recent Discussions

All times are GMT -6. The time now is 12:56 PM.