Kids CAT5 -- help

i have 2 problems:
1) some clown cut thru several of my 22ga UTP 4 pair cat5 cables in the middle of a 100' run -- i need to repair them... i do not want to make new runs... is there an acceptible splicing method (e.g. 110 or 66 punchdown block)

2) i also want to relocate my primary equipment room and would like to "jumper" the 2 rooms together. is it acceptible to run 25 pair cable and terminate each 4 pair grouping at a CAT5/RJ45 cross-connect panel at each end? (see attached file for more detail)
Attached Images
File Type: jpg networkhelp2.jpg (94.0 KB, 54 views)

mkutcher is offline   Reply With Quote
Old 06-14-2003, 04:03 PM   #2 (permalink)
Registered User
 
Wizzard~Of~Ozz's Avatar
 
Join Date: Oct 2001
Location: Hamilton, On, Ca
Posts: 2,369
Wizzard~Of~Ozz is on a distinguished road
Send a message via ICQ to Wizzard~Of~Ozz
You can put 2 RJ45 jacks on them and use a coupler, I'ld say that would be the best bet.

I doubt using a 25 pair cable would be acceptible, the pairs in a cat5 are matched for length and twists etc. if your network is 10base then you might get away with it, but I would not recommend it, instead you can use a 110 punchdown to "patch" together individual cables, or use couplers as I mentioned above (being the recommended method)

Also be sure to beat the clown that cut the cabling.
Wizzard~Of~Ozz is offline   Reply With Quote
Old 06-14-2003, 05:00 PM   #3 (permalink)
Registered User
 
Darius's Avatar
 
Join Date: Dec 2001
Location: Lake Havasu, Az.
Posts: 55
Darius is on a distinguished road
Send a message via ICQ to Darius Send a message via Yahoo to Darius
Well,
you have 2 options:
66 block or 110 block that is CAT5 rated is perfectly fine, as long as you maintain your twist per 1/2 inch at the punch down blocks. I have done that in the past with no degredation on the cables, and they've passed fine with a Penta-Scanner.
As par as a 25-pair cable, they do make it in a CAT5 rated cable, but is pricey. Would be cheaper to run individual CAT5 4-pairs. Also make sure yor runs from eqipment to workstation does not exceed 100 meters end to end (that includes your patch cables).
Good luck to you,
Darius
__________________
UD Herd: P3 933 256meg ram, P200mmx 160meg ram, Ppro 180 130 meg ram: affectionately named:
Workhorse, CALF1, and CALF2
Darius is offline   Reply With Quote
Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Most Active Discussions

Recent Discussions

All times are GMT -6. The time now is 09:08 PM.