Systems Air Conditioning Broke?

Hey,

My home A/C hasn't been cooling this week, so I went outside and checked the unit. There is a big metal hose and a small metal hose that run into the house. I am pretty sure that the small hose used to be hot and the bigger hose was ice cold. Now they are both ambient temperature. The fan is blowing on the unit and the blower works inside the house, but every minute or 2 there is a loud clunk inside the outside unit. My guess is that something is wrong with the compressor.... what do you guys think?

jch216 is offline   Reply With Quote
Old 10-08-2003, 09:46 AM   #2 (permalink)
Registered User
 
Join Date: Oct 2001
Location: Near Chi-town
Posts: 734
Mr. Goodbytes is on a distinguished road
Send a message via ICQ to Mr. Goodbytes Send a message via AIM to Mr. Goodbytes Send a message via Yahoo to Mr. Goodbytes
You should check the yellow pages and call some companies to see if they offer free estimates. I'm not familiar with the workings of home A/C units, but I imagine that if it is the compressor that is causing a problem, you'll need the system recharged after that's repaired.
Mr. Goodbytes is offline   Reply With Quote
Old 10-08-2003, 10:54 AM   #3 (permalink)
Registered User
 
Join Date: Oct 2001
Location: Monett Missouri
Posts: 3,900
Brainchild is on a distinguished road
Send a message via Yahoo to Brainchild
Call Sears, they repair all makes and models

Sounds like the compressor is gone,or it leaked all the the freon out..
__________________
Cheers

B.C.

Hug your kids, you never know:D
Brainchild is offline   Reply With Quote
Old 10-08-2003, 01:44 PM   #4 (permalink)
Registered User
 
Bovon's Avatar
 
Join Date: Oct 2001
Location: Georgia
Posts: 2,233
Bovon is on a distinguished road
Re: Air Conditioning Broke?

Quote:
Originally posted by jch216
but every minute or 2 there is a loud clunk inside the outside unit.
Yep.. that is the compressor trying to come on...or, at least the juice is being applied but the compressor is not coming on. This usually is a dead compressor. If it were just low on freon, the compressor might run..but no cooling. What you are hearing is possibly the start relay energizing to apply AC voltage to the compressor.

If you are as lucky as a double winner of the Power ball lottery...your problem may be only the start relay contacts burned up.
Bovon is offline   Reply With Quote
Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Most Active Discussions

Recent Discussions

All times are GMT -6. The time now is 04:06 AM.